Communities

Writing
Writing
Codidact Meta
Codidact Meta
The Great Outdoors
The Great Outdoors
Photography & Video
Photography & Video
Scientific Speculation
Scientific Speculation
Cooking
Cooking
Electrical Engineering
Electrical Engineering
Judaism
Judaism
Languages & Linguistics
Languages & Linguistics
Software Development
Software Development
Mathematics
Mathematics
Christianity
Christianity
Code Golf
Code Golf
Music
Music
Physics
Physics
Linux Systems
Linux Systems
Power Users
Power Users
Tabletop RPGs
Tabletop RPGs
Community Proposals
Community Proposals
tag:snake search within a tag
answers:0 unanswered questions
user:xxxx search by author id
score:0.5 posts with 0.5+ score
"snake oil" exact phrase
votes:4 posts with 4+ votes
created:<1w created < 1 week ago
post_type:xxxx type of post
Search help
Notifications
Mark all as read See all your notifications »
Q&A

Comments on Why would a standby UPS fail to power devices when there's no power outage?

Parent

Why would a standby UPS fail to power devices when there's no power outage?

+2
−0

I have an ordinary consumer-grade standby UPS with, I believe, ample power for the devices connected to it.[1] It's five years old. For the second time in about a month, I've found my computer powered off and the UPS apparently without power (indicator light was off). Both times, I pressed the power button until the UPS's light came on, then restarted the computer and carried on without apparent problems. In neither case was there a power outage or discernible power disruption (nothing else in the house, including another UPS, had problems).

My first thought was that the UPS's battery had failed (I know they are not immortal), but then I read up on the difference between standby and line-interactive UPSs and found that my mental model was wrong. I thought the house current fed the UPS which then fed the computer, and if the battery in between was bad that would cause problems downstream. According to several articles I read (example), that's actually how a line-interactive UPS works and a standby UPS, in contrast, switches to the battery during a power outage but otherwise just passes house current through to the devices plugged into it. If that is the case, then even if the UPS's battery is failing, I don't understand why that would matter when the house power isn't out.

In the end I want to ensure that I have reliable power to my computer, which might mean replacing this UPS, and I almost asked this question on Power Users, but I'm asking on Electrical Engineering because I'd like to understand how a UPS works and why I'm seeing this behavior. What could cause a UPS to shut itself down and stop passing power through? For example, if it can't keep the battery charged, does a UPS shut down entirely rather than lead you to believe you have backup power? (If so, is that universal, or is it something I can screen for in my next UPS?) Are there diagnostics I could do as an ordinary user without any special electrical-testing tools to understand what's happening?


  1. The UPS spec says 800VA 450W. It's powering a Mac Mini, a monitor (that sleeps when not in use), one external hard drive (Time Machine), a USB hub (keyboard, headset), a network hub, and an infrequently-used printer. This was the biggest UPS I found on the ordinary consumer market at the time I bought it (2018). I don't understand enough about voltage and wattage to evaluate this collection of stuff against this UPS, so maybe I am in fact overloading it? ↩︎

History
Why does this post require moderator attention?
You might want to add some details to your flag.
Why should this post be closed?

4 comment threads

[meta] In the big scheme of things, this is a Power User question. (3 comments)
How often are the power outages? What's the model of the UPS ? (3 comments)
Guesstimate based on typical power draw (1 comment)
I do not know enough to properly tag this question and request help. (1 comment)
Post
+2
−0

I see that manassehkatz has already given you a good answer and plausible explanation for what you observed, so I'll fill in a few other points.

Your battery is 5 years old, so is getting to the point where it could start to fail. I wouldn't expect a 5 year old battery to be bad, but it's to the point where it's plausible. If the battery were 10 years old, I'd just replace it immediately, then see what the symptoms are.

Don't compare UPS batteries with car batteries, even though both are probably lead-acid (in a consumer grade UPS). Cars are very harsh environments for batteries. Car batteries have a lot of robustness built in. This results in a much heavier and larger battery for the same amount of energy storage, but you get reliability in return. They are also over-specified so that they can still do their job with some degradation.

Your UPS battery is probably a sealed lead-acid type, probably 12 V, but I've seen 24 V types used too. These are designed for storage efficiency, deep-cycle ability, and no chemical leakage. They are not designed to handle much vibration or wide ambient temperature swings. As a result, they are physically more delicate.

Individual lead-acid cells produce about 2.1 V when fully charged. A "12 V" battery actually has six cells in series. These cells are packaged together into this unit we call a "battery", but are really independent electrically. A plausible failure mode is that one cell went short inside the battery. This can happen simply over time due to stuff migrating, dendrites growing, or a physical failure. Again, car batteries are physically beefier, so you don't usually see this kind of failure before other effects make the battery no good anymore.

If one cell out of six is shorted, the battery voltage will only be 10.5 V instead of 12.6 like the UPS expects. That's enough of a difference that the UPS would either consider the battery "bad" or too discharged to use, especially when the UPS knows the battery should be fully charged.

Your UPS manufacturer will be more than happy to sell you a replacement battery, at a hefty markup for the convenience and for people that don't feel comfortable doing this themselves. I just looked, and Mouser lists 836 different varieties of sealed lead-acid batteries (https://www.mouser.com/c/power/batteries/sealed-lead-acid-battery). Of course, there it's up to you to know what you need. You need to know the voltage, roughly the capacity in amp-hours, maximum size, and physical connection type.

If you're not comfortable with all that (or can't find someone to help you who is), just get the replacement from the UPS manufacturer, and consider it the cost of having a UPS every 5 years.

If you're more adventuresome, consider that the new battery doesn't have to go in the same physical place the old one did. You can extend the cables to the battery outside the UPS box and have the new battery sitting next to the UPS instead of being nicely tucked inside. That's fine electrically, as long as the cables are thick enough and not too long. I'm envisioning a 1-2 foot extension, just enough to place the battery next to the UPS.

Now you only need to know the voltage and capacity. If you're lucky, the old battery has its spec printed on it, or there is a plaque on the UPS or you can find it in the UPS documentation. The voltage needs to match exactly. Fortunately, it's probably either "12 V" or "24 V". There is some leeway in capacity. I'd say ±50% is OK. Capacity directly relates to run time.

You can estimate capacity from other specs. Let's say you found the battery needs to be 12 V. You have already said the UPS is rated for 450 W, but you also need to know the run time at that 450 W. Let's say for sake of example that the run time is rated for 15 minutes at 450 W.

Ultimately, the battery provides a fixed amount of energy, which the inverter in the UPS converts from 12 VDC to 115 VAC. Energy is power times time. If the inverter is putting out 450 W for 15 minutes, then the total energy delivered is 113 Wh (Watt-hours). There will be some loss in the inverter. For a consumer-grade UPS, let's figure the inverter is 85% efficient. That means the battery has to cough up 132 Wh.

The battery has to be able to hold 132 Wh in this example. However, that's not how batteries are sold. You need to convert this to capacity, which will be listed in Ah (Amp-hours). You do this by dividing the Wh by the battery voltage. (132 Wh)/(12 V) = 11 Ah. So in this example, you're looking for a 12 V sealed lead-acid battery that has 11 Ah capacity. Anything in the 10-15 Ah range should be OK with your UPS. 10 Ah will reduce the run time a bit. Higher capacity will give you more run time, but if you go too high the UPS may think something is wrong when it can't charge the battery as quickly as expected.

History
Why does this post require moderator attention?
You might want to add some details to your flag.

1 comment thread

Battery capacity (3 comments)
Battery capacity
Canina‭ wrote 3 months ago · edited 3 months ago

Aren't battery capacities typically specified assuming some particular discharge rate (and to some specific charge state)? A battery capacity Ah rating might be accurate at 0.05 C but wildly inaccurate even at 0.2 C.

A UPS battery would seem to likely be discharged at a fairly high rate while in use, which leads me to think that the rated capacity (probably at a relatively low discharge rate, unless it's a specialty battery to begin with) might not be very relevant when trying to determine actual useful battery life in that application.

Good battery manufacturers will of course publish datasheets which include more detailed discharge characteristic data such as voltage over time for various discharge rates, but that might not be easy to find for a random consumer SLA battery off the shelf at the home improvement store which might have been rebranded twice or thrice...

Olin Lathrop‭ wrote 3 months ago

Canina‭: Yes, there is more to it than just Ah capacity. However, it's a start, and I was trying to keep things simple.

Canina‭ wrote 3 months ago

Olin Lathrop‭ Entirely reasonable.